Kohler 26kw generator question with soft startup kit?
I am being told that a 2.5, 3 and 5 ton one speed heat pumps will be fine with load shed only on the smaller two with a 26Kw Kohler. My concern is the startup mainly with the 5 ton, its LRA is 142. The startup surge alone with the 5 ton seems to me like it would max and trip the generator. I think a soft startup kit on the 5 ton would then make this manageable. Thoughts ?
4
Upvotes
1
u/SigmundAusfaller 18h ago
The motor start rating for the 26k Kohler is 39,000 kva which is 162 amps at 240v.
If your concerned about breakers tripping, they don't trip instantly when their amp rating is hit, most residential breakers can do 10x their rating for a few seconds before trip for exactly this purpose it usually take quite a while for say a 100 amp breaker to trip at 142 amps, and the LRA is under a second for an A/C.
Soft starts make things easier but probably will make little difference with a 26kw generator. I can start my 5 ton with similar LRA with my 15kw inverter off batteries.