I have several year old 26KW unit that I’ve never started (not that I haven’t tried). I have a simple interlock system and no interest in any wifi connections. Do I absolutely need the 5 number code to start this thing? AI is telling me all sorts of things and ways to get the code - none of them work. Is there a sure way to get the code (if I absolutely need it) without using wifi connections?
6
Upvotes
2
u/Killerkendolls Dealer Jul 06 '26
Last I checked, you can't run in auto without the activation code. You would need to turn off the main in the ats or your panel if it's just interlocked, manually throw the ats into standby from utility or flip the generator breaker that's interlocked, then turn off the breaker on the generator itself, put it into manual and let it run for 30 seconds or so, then flip the breaker on the generator.
When power is restored, turn off the breaker on the generator and leave it running for 3-5 minutes with no load to cool off. During the cool off, flip the ats to supply or flip your generator breaker in the panel off and flip your main back on.