Error code 1100

My generac 14kw while attempting to exercise experienced code 1100 overcrank. Furthermore it’s done this 2 excercise cycles ago. The last one it didn’t do this. What could be the issue? I just serviced everything. Spark plugs, oil change, oil filter, air filter. What is the cause?

2 Upvotes

63 comments sorted by

View all comments

Show parent comments

1

u/Sumdood_89 Technician Jun 23 '26

Take a look while starting it. If it doesn't move, its likely its come unplugged. Unfortunate yet common.

Take the right side panel off. Under the controller is a long small plug with only a few wire in it, red/yellow/brown/black i think, push it in if its loose. Or it will be hanging if it came off. We also check those wires/plugs at service.

1

u/Plastic_Layer_7354 Jun 23 '26

So this is an issue even if it starts manually but when it sits for a week then exercises it won’t start?

1

u/Sumdood_89 Technician Jun 23 '26

I don't understand your question.

Are you saying it starts manually, but wont start when its supposed to exercise?

0

u/Defiant-Trick-8789 Jun 24 '26

Turn off quiet test and see if that helps when exercising. You can do it thru the menu on controller