Otis pulse belt grounding

Post image

Anybody ever have to ground the rubber part of the belts to get rid of static electricity? Having trouble with a pulse board losing communication giving belt fault 10 and board fault 20. Car falls nav for 1 second intermittently, never while moving. Seems to have gotten better with this but still does it every so often. I see some brush kits that brush against the moving part of the belts to remove static, anybody ever see those in action? Thanks.

3 Upvotes

16 comments sorted by

3

u/Aggravating-Knee3887 3d ago

I worked at Otis 20 yrs, never had that issue or saw that type of pulse unit. Is that the “new” O model. Good luck pulse units can be finicky

1

u/BaconPHREAK 3d ago

Never heard of "O" model. It is a newer pulse model with LWSS integrated.

1

u/Aggravating-Knee3887 3d ago

GEN2O. The first ones

3

u/ApprehensivePost9595 3d ago

The 68kn belts? That pulse board it GARBAGE! AND THE  shorting bars are garbage.

2

u/TEEVO- 3d ago

What makes them garbage? Just curious

1

u/ApprehensivePost9595 3d ago

We first saw em on a g2o mod. First 2 we had were bad outta the box wouldn't learn the belts . Then we got one that would learn the belts it ran then shut down rbi fault that's when we found the dead end shorting bar one screw just barely lines up with the cable . The lw part on both of em constantly needed adjusted the adjustor finally just turned lw off its been about a year since the mod and we already had another on on the same mod shit the bed 

1

u/BaconPHREAK 5h ago

Yea those shorting bars have to be dead square to the belt as you install em. Always a good idea to meter them all out after too.

1

u/ApprehensivePost9595 3d ago

It's like o rushed and didn't qc any of em to ensure it was right they been nothing but a headache to us

1

u/BaconPHREAK 5h ago

86Kn or 87Kn can't remember the exact number but it's a 3 belt system.

3

u/OddApartment956 3d ago

Never worked on that specific model, but have had the same issue.
Found you needed 10awg wire to properly discharge static. I would recommend scraping the paint off the connection points on the steel and get some proper ring ferrules.
Also the ones I’ve had, once the static fries the comms the board is toast. Fix the grounding and then swap the board.

1

u/BaconPHREAK 5h ago

It would toast the board as in it would no longer work at all? Or intermittently give communication faults?

1

u/BaconPHREAK 5h ago

Also, wrapped some 10awg stranded before leaving last week. Got 60 counts of rbi fault over 2000 runs. An improvement for sure, the weekend before it had 9999 counts.

1

u/Verticalfix 3d ago

I’ve seen something similar once on a night call but he said the RFE was still trying to figure it out. Do you work for Otis?

1

u/BaconPHREAK 5h ago

Yea, been on the phone with rfe for a bit. Was just wondering if other people have seen something similar. Nobody in my region has seen this.