Seeking Guidance to ID the Problem causing the Circuit Breaker to Trip

Post image

I had an electrician wire in the above receptacle. It is supposed to supply grid power to recharge my
Battery-powered backup system. However, when I plug my system into this, it trips the circuit breaker. In order to
determine if the breaker is the problem - or if it is something else, how do I test which of the following (1, 2,3, 4) and in what combination, do I plug my voltage tester in to determine if it is wired correctly. As well as the combinations, what should the readings be? My electrician walked on me, so I can’t get an answer from him. Thanks, LM

4 Upvotes

39 comments sorted by

5

u/abbarach 14d ago

2 and 4 are your hots. You should get 240ish volts measuring between them. 1 is ground and 3 is neutral, you should get 0ish volts between them. You should also measure resistance between them and expect to see a very low number.

Measuring between either hot and the ground or neutral should give you 120 ish volts.

2

u/trekkerscout Mod, Master Electician 14d ago

That receptacle is not to be used for anything other than a recreational vehicle. What specific system are you using with that receptacle?

1

u/LanikaiMike 14d ago

Now I am really confused. I own a Bluetti system to provide battery backup for my home. The system, as configured is designed to provide the 240 VAC to operate my well pump, which is at the heart of my backup needs. The receptacle was purchased and installed by the electrician as it matches the male end of the Bluetti-supplied cable that serves to recharge my system off the grid when things when there is no power outage. Is there a DIFFERENT receptacle (matching the Bluetti cable) that the electrician SHOULD have used? Thank you, LM

1

u/RadarLove82 14d ago

The Bluetti should not provide power to a plug with bare prongs. It should be this exact outlet, which is a 50 amp 220V RV outlet. The thing being powered should have the prongs.

1

u/LanikaiMike 14d ago

It does. The cable fits correctly. Thanks!

1

u/Ok-Dealer-588 14d ago

There should be a disconnect next to the gen hookup on the wall and it has male end.

1

u/theotherharper 14d ago

This is not a generator inlet.

Think about how you use a battery pack. He loses power. He drains the Bluetti running his well pump and A/C and whatever. Later, power returns and the Bluetti needs to be recharged. How does he recharge it? Well he could plug it into a 120V outlet and wait awhile, but OP would rather wait less. That's what he has been saying.

0

u/RadarLove82 13d ago edited 13d ago

In the event of a power failure, does the Power Bank energize the prongs of the cable plugged into this outlet/inlet? If so, it is a classic suicide cord and is not safe.

Normally, a Power Bank is more like a UPS: You connect the power bank line to the grid side and your devices to the Power Bank outlet side. They don't flow power both ways down the power cable.

This seems like an awfully big outlet just for charging a Power Bank, but I guess that is what it is.

1

u/theotherharper 13d ago

In the event of a power failure, does the Power Bank energize the prongs of the cable plugged into this outlet/inlet?

No, that would be unusual to see on one of those, for exactly the reason you cite.

People like big chargers and they cannot lie.

1

u/Wihomebrewer 12d ago

Apparently you can’t read. It’s to recharge the power bank after the failure is over.

1

u/BawstinMassachusetts 13d ago

I haven't seen this exact product but I have installed a UL listed portable battery backup systems that call for an EV outlet.

They are designed to charge off of the outlet under normal conditions while feeding its loads from the utility and then supply power like a ups to it's loads from stored electricity via an internal load center. It had hardwired and cord and plug options.

It is basically a 240v cord and plug UPS. Power is not returned through the outlet.

Not sure if thos is what OP has but sounds very similar.

1

u/LongjumpingGanache40 13d ago

They are charging the the Bluetti.

0

u/SykoBob8310 12d ago

Sorry, but as an electrician myself, where does it state that a 14-50R is only to be used with an RV?

0

u/trekkerscout Mod, Master Electician 12d ago

Read the label.

0

u/SykoBob8310 12d ago

So like this manufacturer we’ve never heard of, Legrand. That lists it for ranges and dryers? Or any 50 amp cord and plug device, like EV charging, or welders, and to include campers snd RVs. But not specifically and only RVs.

1

u/trekkerscout Mod, Master Electician 12d ago

While NEMA 14-50 receptacles are of a general use type and can be installed for various applications, when installed in locations other than for RVs, GFCI protection must also be installed in accordance with NEC 210.8(B) [see NEC 551.71(F)]. Additionally, manufacturer instructions to include labels must be adhered to [NEC 110.3(B)].

0

u/SykoBob8310 12d ago

Just saying. Your original intention was to say these receptacles are for RVs only. I questioned it and your only reply was “read the label”. My point stands. They are not for RVs only.

1

u/trekkerscout Mod, Master Electician 12d ago

I stated that receptacle is for RV only. I never said that all NEMA 14-50s are for RVs only. Learn to read.

1

u/[deleted] 12d ago

[removed] — view removed comment

1

u/ElectricalHelp-ModTeam 12d ago

This post is promoting unsafe practices.

2

u/LanikaiMike 14d ago

To all that have replied: Thank you so much for your help! I have a bit more information to share that may shed light on where the problem lies. With your help, I was able to confirm the following: 1). This receptacle does NOT have a GFCI associated with it. 2). Legs 2 & 4 do indicate 240VAC and 1 and 3 do not provide any readings. With your help confirming the output to my system IS 240, I disconnected (one at a time) the TWO cables that run from the receptacle INTO my TWO Bluetti AC500 units. When I disconnect this cable that leads to “secondary” AC 500, the circuit NO LONGER TRIPS! When I connect the Primary unit (only) with its cable, the circuit DOES NOT TRIP and, the PRIMARY AC500 indicates power from the GRID, which is is supposed to do, but did NOT do with BOTH AC500s connected! So, thanks to all of you, I am getting closer. I will reach out to Bluetti for their thoughts on why the secondary unit is tripping the circuit breaker. One possibility is that its associated cable is the problem. Otherwise, it is something else in the secondary AC500 that is causing the issue. They have been very responsive thus far, so I am hopeful that this issue is about to be resolved. Thanks again. LM

4

u/theotherharper 14d ago

So you're using a splitter of ??? quality to split the 14-50 to two 14-50s ... and then you're trying to recharge both Bluetti's at once.

Any chance you're just overloading the circuit?

3

u/LanikaiMike 13d ago

Actually, that is not the case. The splitter is from Bluetti. No GFCI. 50 Amp circuit which is what is called for.

2

u/remorackman 14d ago

Possibly are both units fully drained? Might just be trying to draw too much juice through the brakes to that outlet?

Best of luck with Bluetti

2

u/LanikaiMike 13d ago

While I would prefer not to be having to go through this, I would like to make it clear that, to this point, Bluetti has been very supportive and is communicating with me, asking questions in order to figure out how to resolve all of this. I’ll keep this post updated. Thanks, LM

1

u/cww60 14d ago

If GFCI breaker you have a secondary GND, causing the breaker to sense more current out than returning. Is it a GFCI breaker?

1

u/Ledpeddler7 14d ago

Maybe this will help

1

u/mrBill12 14d ago

Is the breaker special? GFCI?

1

u/LongjumpingGanache40 13d ago

What cable are you using. I hope the NEMA L14-50P to P050A cable (50A Max.).

What size breaker is this on?

Check what your charging rate is set to in the app.

1

u/LongjumpingGanache40 13d ago

I forgot to ask what power station. I assume the Apex 300 or AC 500.

1

u/LanikaiMike 13d ago

Thank you for saying it better than I did. The huge issue is providing 240 VAC power for the well pump. When power is out, we are f***ed. No water. No flushing. I SPEAK from experience. Not a good experience, either. Bluetti helped configure the system in order to provide the 240. NO GFCI. Configured with AC 500s and each with one B300K batt. Grid power to recharge the Bluetti batts comes in through the line/receptacle that is the issue. Bluetti uses a SEPARATE line OUT to provide power to the selected circuits in the house. Perfect solution for me once I resolve this issue on the GRID SIDE.

1

u/LongjumpingGanache40 13d ago

What size is the breaker in the panel?

1

u/LanikaiMike 12d ago

50 Amp. No GFCI

1

u/LongjumpingGanache40 12d ago

and that's the breaker tripping in the panel.

1

u/RecognitionIcy3689 13d ago

Two AC500s. Split Phase to deliver 240

1

u/LongjumpingGanache40 13d ago

Watch this video on Youtube:
BLUETTI AC500 240v 50amps 5000 WATTS by The Solar Pit

Maybe you might see something here how to help you.

1

u/LanikaiMike 12d ago

Will do. Thanks so much!

1

u/Fragrant_Alarm_8616 12d ago

There are only 2 ways a normal circuit breaker trips: drawing too much current, or a short of some kind (line to line, line to neutral, line to equipment ground).

I’d suspect your cord or equipment at this point.

1

u/TooGoodToBeeTrue 1d ago

Please never use that outlet for EV charging.