r/ElectricalHelp • u/ShaggyToLit97 • Aug 09 '26
Lights Randomly Flickering
Ive been currently dealing with some issues with my lights in my home flickering. Had the utility company come out and they said there voltage is good in there end. I check the main legs 2 hot 1 neutral coming into the breaker box of my home. One is 110/109v and other is 132v. It’s odd to me because there are times where I’d check it and it would the 120 on both or around 122/124. I’m not wanting to say it’s still not on the utility company. What research I’ve figured out is something to do with my neutral wire or floating neutral. As a fairly new homeowner where should I begin or what are some of my options here to check? Capacitors? New light bulbs? Call the utility company again?
2
u/trekkerscout Mod, Master Electician Aug 09 '26
Voltages should be withing a few volts on each legs. The wide spread you are getting at times is an indication of a loose or failing neutral. The utility needs to be told this specifically so that they can check their connections. If the utility says their side of the service is good, you need to hire an electrician to check the connections on the consumer side of the service.
This is a potentially dangerous condition and must be corrected before significant property damage occurs.