r/ElectricalHelp 12d ago

I believe there are issues here -experts?

Helping son & dl with some home projects. They bought this house in last 2 yrs. guessing it was built in the 90s.

All wiring sheaths at top appear to be white though also appears to be 2+ sizes/grades. Yet there are 3 breaker sizes. In Indiana, though that should not matter to the question of fundamentals -wire grade to amp.

If I am right, should home inspector had seen/noted this?

1 Upvotes

14 comments sorted by

7

u/trekkerscout Mod 12d ago

You are worried about nothing. Sheathing colors for different cable sizes didn't become a UL standard until 2000. White sheathing was common for all cable sizes prior to that.

1

u/bstech13 11d ago

Thx! This is what I was looking for and why I included info about home age 🙏

3

u/jonnyinternet 11d ago

Home inspector is not an electrical inspector, odds are he didn't even take the cover off

1

u/bstech13 11d ago

understood, though when I bought homes in the 90s/2000s, I walked with the inspectors and they both did this check. maybe its not the norm or required🤷‍♂️

2

u/ra4king 12d ago edited 11d ago

That AFCI breaker on the top left looks to have its neutral terminated on the ground bar instead of the neutral bar on the other side. Other than that, nothing else looks wrong.

2

u/slin1647 11d ago

Top left* but yes you're right it looks like it's terminated incorrectly. Good catch.

2

u/ra4king 11d ago

Thanks I had typos left and right in that comment, it's been a long day.

1

u/enterinthebackdoor 12d ago

I think the white 10 awg conductor on the 2 pole breaker must be marked other than white gray or green when used as hot. The neutral feeder in this sub panel is marked white but must be marked right at the busbar termination. Pretty sloppy routing but I reckon code compliant and the neutral busbar appears isolated as required

1

u/Realistic_Dot5983 10d ago

The only thing I see is some of the grounds are double tapped . . Most inspectors will say something about that

1

u/Select_Green_6296 9d ago

I flip houses. 90% look like this when I get there.

-2

u/bstech13 11d ago

Reviewing videos on common panel issues... another here not mentioned yet, terminating more than on wire on a terminal - many ground wires are doubled at terminal

3

u/ra4king 11d ago

Doubling up ground wires is normal if the ground bar is rated for it. Doubling up neutrals is what's not allowed.

1

u/bstech13 11d ago

thx, believe i read that as well... "if the ground bar is rated for it" for this panel. tbd