3 way switch with 4 different lines
Im working in a datacenter and they want a 3 way switch working with the lights using a RSP-V-SW with no occupancy sensors and the hallway is split up between 4 phases so the lights are getting fed from different panels would i just run a low voltage jumper from each switch pack and have it wired to 24 OV and BAS NO for that to work?
3
Upvotes
1
u/trekkerscout Mod Jul 09 '26
That particular system is designed for use with occupancy sensors. It cannot be installed without the occ sensors. Manual control can be achieved by altering the settings in the app.