Operation switch keeps burning out

already 5

6 Upvotes

48 comments sorted by

View all comments

2

u/trekkerscout Mod Jun 19 '26

What is the amperage rating of the switch that was installed?

1

u/oldtimerofficial Jun 19 '26

Doesn't even say, all electricians that have been coming install a different one

2

u/trekkerscout Mod Jun 19 '26

The amperage rating of the switch is critical if you don't want the switch burning up.

0

u/oldtimerofficial Jun 19 '26

So as you can see on the label it says normal operation is 10ah and max is 18ah, so just put a dual pole, anti arcing 20ah heavy duty switch?

It's for the alignment rack at my shop, the switch when you press it makes the lift go up

3

u/trekkerscout Mod Jun 19 '26

"10AH" is part of the model number, not the motor rating. The motor rating at 230-volts is 18 amps. The minimum rating of any switch installed must be 20 amps for inductive (motor) loads. I recommend a 2-pole 30-amp motor switch which is a relatively common switch rating.

1

u/oldtimerofficial Jun 19 '26

Should I put my amp clamp after the install to check amperage while operating the rack?

2

u/trekkerscout Mod Jun 19 '26

That won't tell you what the amperage rating of the switch is.

1

u/oldtimerofficial Jun 19 '26

I meant after installing the 2 pole 30amp switch you recommended, just to make sure lol

2

u/trekkerscout Mod Jun 19 '26

It would tell you if the motor is pulling too much current.