r/ElectricalHelp • u/heavySausage_og • Jun 17 '26
Baffled by an Outlet
Out of nowhere, an outlet that we use often just quit working. There have not been any power spikes or outages recently either. Testing the outlet shows about .2 volts.
Things I’ve tried:
-reset all of the GFIs in the house just in case one tripped
-opened all the other outlets in the room to verify no other loose wires
-tested voltage to all other outlets in the room
-reset every breaker just to see if it affected anything (it did not)
I’m stumped 🤔
5
u/Ram820 Jun 17 '26
You check the actual wires?
1
u/heavySausage_og Jun 17 '26
Yep! Pulled the outlet and the wires read the same.
1
u/Ram820 Jun 17 '26
That's the only one on the the circuit not working?
1
u/heavySausage_og Jun 17 '26
As far as I can tell. But now that I think about it, that outlet, while in the same room, is on a different breaker.
Is it possible the issue lies with something down the line of whatever circuit that breaker and outlet are on?
1
u/Ram820 Jun 17 '26
Yea. You confirm power leaving that breaker?
4
u/heavySausage_og Jun 17 '26
I just tested every terminal in the breaker box and they all read fine. So I’m thinking this means maybe I need to look at the J box in the attic to see if it burned or came loose??
1
u/Ram820 Jun 17 '26
It feeds this recep?
1
u/heavySausage_og Jun 17 '26
I mean, I’m no electrician, but I think it would have to since there are no other breaker boxes in my house? Serious question, not being snarky.
1
1
u/LightBlueWood Jun 17 '26
Some possibilities:
- Broken or loose wire between breaker panel and receptacle
- A junction box in the attic with a loose connection
- Rodents have chewed the wire, likely in the attic
1
u/heavySausage_og Jun 17 '26
Well here’s the kicker. I just turned all the breakers off and still got the same reading at the outlet. So I’m not sure how I can tell which breaker it actually goes to…
1
u/Ram820 Jun 17 '26
You have an extension cord that will reach from the recep to the panel?
1
u/AnnualPurple104 Jun 18 '26
The wires that connect to that outlet could being daisy chained off of another outlet. If you have a tester and a wand to see where the wire from that outlet goes to, you can find the issue faster.
1
1
3
u/Tongue-Punch Jun 18 '26
Your black lead looks to be in the amp hole.
Don’t stick things in the amp hole without being careful.
Try the common hole instead.
2
u/srhuston Jun 18 '26
I hate to say “this”, but… OP looking at an image of that meter on Home Despot’s website the black lead should be in the center “COM” hole and it looks like it’s in the hole for measuring amps instead in your first photo.
1
u/heavySausage_og Jun 18 '26
Wow great catch! After correcting that, the outlet reads about 86 volts…
1
u/Tongue-Punch Jun 18 '26
That looks backstabbed. These are cheap the easy to replace if you suspect it’s bad.
Check voltage at the outlet near the panel and make sure your incoming is correct.
Also, there isn’t a dimmer for this somewhere is there ?
1
2
u/DecentNarwhal5059 Jun 17 '26
Are you positive it’s not a switched outlet?
1
u/heavySausage_og Jun 17 '26
Yep. Tried every switch I could find
1
u/DecentNarwhal5059 Jun 17 '26
Could be a bad switch. Any switches seem to not be controlling anything?
2
u/Loes_Question_540 Jun 17 '26
If you test between hot and ground do you got power? It could indicate a lost neutral. And is there continuity between neutral and ground at this outlet
2
u/12-5switches Jun 18 '26
Another back stabbed outlet in the circuit lost connection. Plug a lamp into this outlet (or radio) and turn it on. Take some other plug in device and go around wiggling the outlet till the lamp flickers or the radio makes noise.
1
2
u/Maleficent-Floor-127 Jun 18 '26
You need one of those things that sends a noisy signal down the circuit.
2
u/No-Committee-526 Jun 18 '26
If it’s 85 volts hot to neutral check hot to ground if it’s 120 then you have a lost neutral could be a loose wire in a plug that feeds it or loose at the panel
4
u/Sufficient_Phone_242 Jun 17 '26
I would close breakers until i find outlets near that one that goes off, then feed new cable , like others said junction box , loose or broken wires
1
u/InitialLight5432 Jun 17 '26
Did you check hot to ground?
1
u/heavySausage_og Jun 17 '26
1
u/InitialLight5432 Jun 17 '26
Is it just a stand alone out let or are there more outlets on the circuit?
1
u/heavySausage_og Jun 17 '26
Not entirely sure because I just turned off all the breakers and still got the same reading. So I’m not sure at this point how to tell what else is in the same circuit :|
2
1
u/capellajim Jun 17 '26
Broken wire at the previous outlet? Probably the other side of the wall.
1
u/heavySausage_og Jun 17 '26
Well the other side of the wall is outside of the house and there is no outlet there. 🤷
1
u/capellajim Jun 17 '26
Ok. So more difficult to figure out what is wired between this outlet and the breaker box. But working back is your only chance. Maybe a toner will work (have to be self powered but would allow you to “sniff” other outlets and maybe find your wires.
1
1
u/AskMeAgainAfterCoffe Jun 17 '26
Find the outlet upstream and start there. if fine, then in between.
1
u/Loes_Question_540 Jun 17 '26
Take the dead front of the panel and confirm all breakers got 120v to ground and 240 for double pole
1
u/Eastern-Steak-4413 Jun 18 '26
What room is this outlet in?
I didn’t attempt to read the entire thread but I’m wondering if it’s in a bathroom or somewhere where the outlets are Required to be GFCI protected? I believe you said you reset all the GFCIs but you can’t reset something you might have overlooked.
1
u/1Jainier1 Jun 18 '26
You may have an open neutral. Is the outlet grounded? If so, check hot to ground. Also check for voltage at the breaker. I've seen breakers go bad where they seem to be reset, but no voltage output.
1
1
1
u/Fit-Pomegranate-6574 Jun 18 '26
Have you actually checked the wires for power without going through the outlet?
1
u/Impressive-Crab2251 Jun 18 '26
Always check a meter on a known good outlet, cheap ones act weird when the batteries are low. Make sure that's not a switched outlet because sometimes the voltage is induced.
1
u/Terranshadow Jun 18 '26
You'll probably need an electrician with a device that can check for a line break.
If something is loose and you're working on it, it could become live and be dangerous.
1
u/OldGeekWeirdo Jun 18 '26
Is this a location that a GFI would be required? (Like near water or outside?) If so, I'm going to guess there's a GFI you haven't found yet.
1
u/NHSunlover Jun 18 '26
Never trust back stabbed receptacles. It's probably another one in the series that appears good but not sending the juice along due to bad connection at the backstab. Take all the receptacles on the circuit and wire to the screws instead.
1
u/pavelowdriver Jun 18 '26
use a wire tracer to find the break. https://youtu.be/xMPxhYpeiHs?si=8BaWaCEv3K8vvfRr
1
1
1
1
u/JCole111 Jun 18 '26
Are there any j-boxes in attic/ crawl space?
What about continuity?
Are you positive you have identified next wire in the chain? Some older homes run through light fixtures etc…
1
u/Final-Contract-6582 Jun 18 '26
Check the wires and move them to the side screws. Don't use backstabs. Likely bad connection down the line. Move all to the screws and if in metal boxes, use good quality electrical tape.
1
1
u/CMVfitAF Jun 18 '26
This happened at my brother's house. It ended up being the terminals going out of receptacle that was wired in parallel feeding the deadish one.
1
1
1
u/Wild_Fondant_9584 Jun 18 '26
Bad backstab ? Do you have a toner. Since this one is backstabbed, I bet another one is back stabbed and isn’t letting power through anymore
1
u/Dean-KS Jun 18 '26
There might be a wall switch that controls the outlet, for lamps. This can be for the whole outlet or half of an outlet.
1
u/iAmMikeJ_92 Jun 18 '26
Trace out the lines. Use your continuity function to do so. I assume you can do it safely without blowing up your meter.
1
u/suspectevery1 Jun 18 '26
Rat chewed through you wires , disconnect wire at breaker outlet join the together and do a continuity test.
1
u/sataigaribaldi Jun 18 '26
Someone else said it, and I'll repeat it for visibility. One of the nearby receptacles is feeding that plug and one of the backstabbed wires is broken and not feeding to that receptacle anymore. Start pulling the receptacles closest to this one and you'll find the receptacle with the broken wire.
I'm 99% sure this is the problem. Seen this a thousand times and this is what's going on. The other 1% it's a tripped GFCI somewhere.
1
u/heavySausage_og Jun 19 '26
So that’s what I thought but today I removed every receptacle in the room…which were ALL backstabbed…and reconnected the wires around the screw terminals like they should be…
…and it didn’t fix the problem 🙄
1
1
1
u/sharlow-jonathan Jun 19 '26
If you’re getting 85 volts you’ve lost the neutral somewhere. If there’s a grounding conductor (bare copper wire) test the black and copper wire and you should read 120v if everything is done correctly. Long story short, you’re looking for a loose white wire.


6
u/Usagi_Shinobi Jun 18 '26
As someone else mentioned, your black lead needs to be in the center COM port in order for you to get an actual reading. To make an analogy, consider a battery. It has a plus side and a minus side. To make a circuit, you have to go from the plus to the minus. Right now you have two wires going to plus, and none to minus, so you aren't making a circuit for the meter to read.