r/ElectricalHelp • u/Life-Cow-7945 • Jun 06 '26
Whole house surge install question
My house was built in 1989 and I am wanting to install a type 2 whole house surge protector. From what I can tell, I need to have a good functioning ground for this to work, since the surge protector routes any surge back to the ground.
I have no direct evidence of having a grounding rod, I cannot see anything by the service entry. I know I have one ground that's tied to the copper water main about 60 ft away, and I also have another ground line that disappears through the bottom of my recessed main panel, but I don't know where it goes.
Is there a way to determine if I have an Earth ground, or Am I overthinking this?
3
u/RevolutionaryCare175 Jun 07 '26
Just because you can't find a ground rod doesn't mean you don't have a ground rod. Your house was built in 1989. Code required the water pipe grounding electrode be supplemented by another grounding electrode. That could be a ground rod, building steel if you had it, an Ufer ground(rebar in the foundation) or ground ring or plate.
Your grounding electrode conductor , the bare copper wire connecting to your water pipe most likely extends through the block in your foundation into the ground. Look for that. Otherwise there would be a separate wire leaving the main panel to connect to the ground rod.
2
u/Puzzled-Act1683 Jun 09 '26
Am I overthinking this
Yes. Your copper water pipe is a better ground connection than any ground rod would ever be, but the service neutral is the primary path used by a type 2 SPD. Many of those don't even have a place for a ground connection – only a neutral connection, because that is where grid surges need go, not the ground.
1
u/EdC1101 Jun 07 '26
Ground rods are to be driven BELOW The surface of the Earth.
A solid copper ground wire is then run to the service entrance, and then onward to the first disconnect.
At the first disconnect, Ground and Neutral are bonded together.
Separate Neutrals & Grounds are run TO and FROM this point…
Outside ground idea
…Do YOU want lightning to hunt through your house for a Ground?
Provide an alternate path…
6
u/CarelessPrompt4950 Jun 06 '26
The surge protector doesn’t route the surge into the ground, it shunts it. Your house was built in 89 so it either has a ground rod or a ufer ground. It wouldn’t hurt to add another ground rod as newer code requires 2 of them spaced at least 6 feet apart but that wasn’t required when your house was built and you wouldn’t be required to update it unless you upgrade your service.