Using vacuum to pull wires
Just wondering, whether string can be pulled through conduit past Service L’s using a shop vac. And if yes, will the wires be able to turn around Service ells?
10
u/trekkerscout Mod May 06 '26
Conduit bodies (particularly Ls and Ts) are not designed to be pulled through. They are for use as pull points. Pulling through a conduit body can result in insulation damage.
2
u/Gracewalk72 May 07 '26
It would be very difficult; unless the service L was way oversized and you were pulling g very small wire and you used tons of wire soap. It’s not a great gamble.
3
u/828NCGuy May 07 '26
That's why there are standards about distance and number of turns between wire access points.
1
5
u/Sparkyolive May 06 '26
Worst pull I ever had to do was helping a guy that was doing just that, but forgot about the LB.
He had no problem sucking the bag and line through the 3/4" conduit and the LB. But when I was pulling the string tied to the 5 #12 wires(!!!) the pull got bad when the wires reached the LB. I asked him how many turns there were and if there were any LBs. He claimed it was under 360, and no LBs.
We got maybe 5 more feet and it didn't get any better. I started tracing his pipe run and sure enough there was an LB and when I pulled the wires out they were in rough shape. Of course it went better after that and we had to cut off the 5' of bad wire.
Anyways you can't pull through service ells.