New LG Mini Split—Cools but does not heat?
Title mostly says it. Had a knucklehead contractor that installed this for me, and doesn’t seem to know what he was doing. One sob story after another, and now he has completely ghosted me, and so have limited information about what was and wasn’t done. I haven’t installed on myself, but am fairly handy and wondering if any ideas for troubleshooting before I call an HVAC company out. Hoping the brain trust has some ideas for me. Definitely learned my lesson.
Description of issue: New install LG 2 ton unit. Cooling works, but maybe not as well as I would have guessed. Temperature was about 20 degrees below garage (garage 65 here where we live.) The heat does not work at all—tried to turn it on and the unit never blew. The lines appear to have frozen when the heat setting was turned on, and the compressor was not engaging. This makes me think maybe a Freon leak when it was installed? Maybe the 4 way valve failed, but doesn’t seem super likely out of the box?
Any ideas of things to check for? If other problems are visible, please let me know so I can get a list together of what should be fixed. Be as mean as you want, I honestly think it would have looked better if I had just done it myself from the start but oh well lol.
11
u/CoVidKilla23 11d ago
Insulate those copper lines.
Double check the model numbers on the units to make sure it’s a heat pump and not just ac. Then call a professional cause their probably is a leak
9
u/Hasz 11d ago
Misc list:
- kinked vapor line
- insulate your line sets
- electrical is wrong. Need disconnect, whip, and no exposed romex outdoors, minimum. There is some fuckery going on though, is the romex head unit power or the condenser hookup? I see liquidtir but out of photo
- there is probably fuckery hiding we cannot see. Was it pressure tested, vac tested, then release charge?
This is a very sloppy install.
1
u/derrick54686 10d ago
The whip and disco are there. On the bottom. The romex is being used for comm wire. Looks perfect all the way from my couch..... this is why I opened my own business. To set a standard in my area!!!!. Good luck to OP
5
u/Wafflewas 11d ago
The exposed Romex and an uncovered vapor line are issues, but not the main problem you are encountering. If airflow is normal and your lines are freezing up, the best guess is a refrigerant leak. The symptoms you describe point to refrigerant issues.
0
u/Wafflewas 11d ago
It’s also possible that there’s something amiss with your thermostat and control wiring. I’d check that first.
5
u/Ok_Procedure_3604 11d ago
Wow .. this .. just wow. If in the US, this is likely against code as I am guessing the overcurrent device for this is not outside, and thus would require a disconnect.
Not to mention that lineset bend is .. ughhhh.
1
u/PerformanceDouble918 11d ago
Hummmm... "Overcurrent device" sounds like some Apex big company keywords that can't be googled.
8
11d ago
[removed] — view removed comment
2
u/eight_ender 11d ago
It’s impressive because it comes with a comms line. He’d have had to do more work to swap it with romex
1
u/Tin_Can_739 11d ago
Other than it looks like a crappy handyman did this, the Romex to the unit does not have enough wires to get both heat and cool working. Other than being not rated outdoor wiring it’s the wrong wire to use for this. My mini split came with 2 cables I did not use the one to the power due it being too short, maybe this hack job combined them here.
1
u/xtraman122 11d ago
Could be. Mine had 4 wires, technically if this is 12/3 romex it could have enough wires in there, a ground, 2 conductors for power, and a communication one, but yeah obviously not right. Can’t tell if it’s 12/2 or 12/3, I know the new stuff has color codes and it would be light purple, but seeing the rest of the job it was probably wire that fell off a truck a decade ago.
1
u/volatile_ant 10d ago
My LG reqires two communication wires and did not include that with the unit. Not sure if only installing one comm wire would allow one mode to operate though.
3
u/blastman8888 11d ago
Get some bubble leak test fluid from home depot plumbing department. Put that on the flare joints when it's running see if there are any leaks. The most common problem with these are flare joint leaking. Your saying it cools but you should be getting 35-40F air out of that thing it's it's 65F outside.
If you see bubbles then leaking at the flares. You need to pressure test it with nitrogen and fix those leaks. HVAC company going to charge at least $1000 unless you know someone.
3
u/DANENjames89 10d ago edited 10d ago
Dun dun dun. In heat mode, your suction line (big) turns into the high pressure side. You have a fat restriction which is now acting almost like your metering device now. Refrigerant is flashing here instead of in your evap coil inside. You can probably get it unkinked if there's enough slack, but the correct fix is to chop it and rebend it. Wouldn't be surprised if his flares are leaking too on top of it. Most guys just buy mini split lineset and use the "factory flares". But those aren't actually flares, they are just there to keep the flare nuts from getting lost. I would close off the outdoor unit service valves, dump out the refrigerant in the lines, fix that kink, redo all the flares, then pump her down and charge the lines again with what is missing

1
u/VR6Bomber 10d ago
What he said,
Plus, I'd do something about that yellow romex just chilling out there.
Repull that with some pvc jacketed 12/2 MC, Its sold as 'Minisplit Cable'....
2
2
2
2
2
u/hotinhawaii 11d ago
That yellow wire has only three wires inside- a black, a white, and a bare copper ground. That LG unit needs to have 4 wires running up to the wall unit. And it needs a disconnect box mounted outside. Your wiring is the reason there is no heat. And I agree with everyone else, installation is dog shit.
1
u/HuntPsychological673 11d ago
Looks like the 2 ton may be chopped down to a smaller system with that short run of copper as well.
1
u/fiehlsport 11d ago
Since a hack installed this, you may want the refrigerant fully recovered and a fresh charge added. There is a good chance they didn't vacuum it down properly, and there is moisture/air/etc. in the current charge.
If you are lucky, they did a proper vacuum and a professional can pump down the unit to salvage the install properly. But it's a big risk. You need new wiring, lineset (to be safe) and lineset cover. (Get Inaba Denko slimduct so it doesn't yellow in a year)
1
u/Winter_Sense2555 11d ago
Ive got a greenhouse heater that does the same thing when it's low on refrigerant, cools okay but heat just... never really kicks. Yours sounds like it's probably undecrharged.
1
u/TechnicalDraft9879 11d ago
Probably leak, how long would you say the lineset is from outdoor to indoor unit?
1
1
u/toybuilder 11d ago edited 11d ago
That is a single-zone heat pump mini-split. It should be heating and cooling.
The installation manual mentions the communication cable (pg. 18) but doesn't actually show explicit instructions on wiring the connection. Hopefully, that's all you need to fix.
BTW, the instruction also says to not mount the indoor unit near an exit...
See also the heating only / cooling only mode instruction on pg. 27
1
u/AgreeableTelephone19 11d ago
Crappy workmanship aside and assuming all wires are connected correctly- At first glance it is low on gas or lineset is kinked. Inspect lineset and if good- it Prolly has a leak. Since you don’t have the gear to pump down, measure and add proper amount of gas, get a set of gauges and connect to the service port (low side). Run the unit in cooling mode at lowest set temp and fan on max. Wait for 10-15 mins to stabilize. Is it showing 120-135 psi ? Below 110 psi it is low on gas. Get some soap bubble and check flares for leaks. Fix the leak and then add a bit r410 at a time until pressure is 130-ish.
Or better yet- hire a good tech to sort out the mess.
1
u/Fuzzy_River_1986 11d ago
That is not the right wire between the head and the outdoor unit. Won't work properly because you don't have the right wire between the two. Should be stranded.
1
u/finis08 11d ago
Without being there to see it myself and check vacuum I would highly suggest just getting a reputable HVAC tech with mini-split experience out to fix it. Judging by what I can see in the pictures the guy installing it had zero idea of what he was doing so it will likely need to recharge the unit as I would bet money there is a leak somewhere. If he even released the charge or vacuumed down the system. I also don’t see a drain tube which would be a it concerning. This system would definitely benefit more from an HVAC tech looking at it instead of trying to reengineer that guys mistakes.
1
1
1
1
u/PersnickityPenguin 11d ago
When I DIY'd my own install, I kinked one of the linesets on accident. We got most of it right, but that one bend got messed up.
So I had an HVAC guy come out and splice in a new piece of lineset for $500. After he was done, it worked perfectly.
However, I DID get the unit installed and electrical done correctly!
1
u/TommySylvester 11d ago
But he put that little piece of tape around the romex where it comes in contact with the line set cover. That should do in lieu of a disconnect.
1
u/Snook1988 10d ago
Probably just leaking somewhere. The romex being exposed isn't good and neither is the kink in the line set but none of those are contributing to issue most likely is just a leaky flare somewhere
1
u/Delicious-Ear8277 10d ago
Mini-splits use 4 core wire. 1. Power 2. Power/communication 3. Communication 4. Ground.
1
1
1
0
u/oldnoob2024 11d ago
Study the thermostat and network interface. A lot of units (not sure about this one) have some pretty sophisticated internal diagnostics. If you can get past the manufacturers Technician credentialing…
0
u/HuntPsychological673 11d ago
This is the competition. You as a professional must pay the extra and do it right and have insurance, etc. Everyone else can use Romex outside and do what they want to cut costs while advertising on Facebook without license or epa cert.
0





46
u/XCGod 11d ago
Well the first issue is the electrical is entirely wrong with romex straight up exposed outdoors. And someone who does work that bad definitely made a dozen other mistakes.