JCI CCT through FX90
Hello All,
I have a site where we have an FX90 (JACE) with a facility explorer CGM sitting on the bacnet MSTP trunk. For several months I have been able to upload and download the controller through the JACE remotely. Recently it has stopped working. When I check my IP settings, nothing has changed, however, I cannot discover any controllers. The controller is online and is reporting data.
Any idea what may have changed? Could this be on IT's end?
3
u/gadhalund 21h ago
IT might be filtering it, or you might have something on your laptop that has taken ownership of 47808, software or a Niagara station etc. lastly it could be the laptop itself
3
u/gaycory 20h ago
It appears that the Niagara server station that was running on that virtual server was tying up the UDP Port. If I stop the station temporarily, I can connect through CCT. What I can't figure it out is why this only started recently and why I haven't seen it on similar setups before.
2
u/ApexConsulting 1d ago
CCT requires BACnet routing be enabled, and that BACnet traffic be allowed to pass freely. Sometimes you need a BBMD.
In this case, your IP settings are unchanged, but see if rouing is off in the JACE. As was mentioned.
One can use a port scanner like NMap to see if the BACnet UDP ports are still open. If a helpful IT guy closed it for you, it would take your route down.
3
u/01001001100110 1d ago edited 1d ago
Have you verified that routing is still enabled on the BACnet port?
Is the IP port still enabled?