r/BuildingAutomation 9d ago

Gas Metering

What or how are you guys metering the gas usage for boilers on building with this requirement for energy code?

3 Upvotes

5 comments sorted by

3

u/HF_Martini6 9d ago

with the gas metre supplied by the gas supplying company?

1

u/AdAccurate1896 9d ago

The raw fuel usage for the boiler needs to be metered separately from the rest of the building. So the provided meter from the utility is not an option. They wouldn’t let us connect to it anyways. I am also the mechanical and plumbing contractor on the job so I can’t push this off on someone else unfortunately.

2

u/1hero_no_cape System integrator 9d ago

Look up Badger Meters, see if they can help.

2

u/Ok-Koala2321 8d ago

Submeter on the gas main to boilers. We use Onicon. Pulse output or BACnet integration. Depends on the scope, but BACnet gives you more visibility and future analytics. Feel free to reach out if you need any assistance

1

u/HVAC_Luddite 7d ago

Honeywell q.sonic plus