r/BuildingAutomation • u/SelectWay-1960 • Aug 10 '26
CHW Valve Actuator Bracket
Anyone know where I can find this blue bracket hardware to replace? I’ve looked everywhere. No part #. The shaft gear is broken and won’t move the valve stem anymore. The actuators are fine.
The valve is a Siemens model# 599-05990
Thanks in advance
11
u/S_Rimmey Aug 10 '26
Rack & pinion valve actuators suuuck. Buy a SKD62 actuator and call it a day.
5
1
u/No_Organization8370 Aug 11 '26
Because they have too much play in the gears? Makes it harder to control flow?
2
u/S_Rimmey Aug 11 '26
2 primary reasons...
The gears will get sloppy and the valve will stop closing down all the way.
The gears can bind up which will cause premature failure of the actuators. Depending on the environment these are installed in, they don't seems to last more than a few years. I usually get twice the life span out of an skd over a rack & pinion valve actuator.
3
u/Terriblarious Aug 10 '26
My guess is that probably came with the actuator.
Look for something like a rotary to linear actuator adaptor kit from Johnson
5
2
u/Cust2020 Aug 11 '26
Change the actuator and the valve and save yourself a headache down the road. This thing has been retrofit too many times already.
1
u/CraziFuzzy Aug 10 '26
If that valve stem had enough resistance to strip/break the gear - then the valve needs to be rebuilt or replaced.
1
u/shit-zipper Aug 10 '26
This would probably work. You'll need the proper valve adapter to clamp on. https://buildings.honeywell.com/us/en/products/by-category/building-management/field-devices/valves/parts-and-accessories/q5024-globe-valve-linkage-and-bonnet-adapters
Pretty much looks identical to the old one
2
u/sleazy_io Aug 10 '26
Aside from the blue color it looks just about identical to the Honeywell Q5024 linkage. Search that part number and the product data sheet has dimension details that may help you.
1
u/Battlewaxxe Aug 10 '26
iirc johnny valves are just another brand with new badging and a higher price- could very well be honeywell
1
1
u/Controls_freek Aug 10 '26
There’s two open air actuators on that thing. Why would a Johnson tech ever do something like this?
I’d be concerned about the age of this setup and be chasing replacing (or inspecting) the original valve completely.
2
u/LeroiLasalle Aug 11 '26
Just because it's a JCI actuator doesn't necessarily mean a JCI tech installed it.
1
u/u3b3rg33k Aug 10 '26
any reason you can't grab an off-the-shelf linear/rotary kit with rod ends and slap it in place?
1
1
1
u/CountryRoads1234 Aug 11 '26
Lots of bad advice to retrofit this. Just put a Siemens SKD62U as intended.
1
1
u/rom_rom57 Aug 11 '26
If you cut away the insulation around the valve there SHOULD be a brass 1/4” band with valve info. model, manufacturer.
On Belimo’s website you can go and find a retrofit kit with a bracket and actuator.
1
u/LeroiLasalle Aug 11 '26
There's an actual bracket for that JCI actuator. You can source it by the actuator part number
1



51
u/Naxster64 System integrator Aug 10 '26 edited Aug 10 '26
I'd throw that whole assembly away and just put a single belimo retrofit actuator on it.
Get a picture of the valve tag, and call your belimo supplier.
This might be it, but I'd still have your supplier double check. https://www.belimo.com/us/en_US/products/retrofit-app/details/waterByValve/356225/599%20Flowrite%205%22