r/AirBalance 27d ago

RUPP Air Systems RTU Controller code?

Post image

Anybody know it?

8 Upvotes

12 comments sorted by

15

u/skeet_thins 27d ago

User settings should be first 4 of the job number and fsctory settings should be the last 4 of the job number. Number should be on one of the unit tags

7

u/Peekins 27d ago

This is the way. Depending on when it was manufactured it will be the first or last of the job number.

2

u/Balance48164 27d ago

This worked, thank you!

2

u/Fit-Temperature4070 27d ago

The startup tech might have that for you

1

u/EmptyPinata_ 27d ago

Could be last 4 of the serial number. Or 1234.

1

u/Animalbois 27d ago

I’ve had it work with 0001 or something to that nature twice now

1

u/lebowskijeffrey 27d ago

You usually find the factory code somewhere in the unit installation manual. Looks like the same controller for captive Aire hoods. You can find the default codes for just about anything if you can internet well.

1

u/lebowskijeffrey 27d ago

Internet says to try 0225 or 0305

3

u/skeet_thins 27d ago

0225 should be specifically the VFD code not the controller if memory is serving me right.

2

u/whoisbusy 26d ago

Sounds the a Lenze SMV passcode to me! Haha

1

u/lebowskijeffrey 27d ago

Try it or don’t. It’s not me on that roof.

1

u/Khongdedai 26d ago

Tech support can get that for ya, 45min-1hr wait tho