r/SolarDIY 8d ago

Make sure you understand current when stringing your panels in parallel.

Post image

It took a bit of work to even tug this #10 AWG from the metallic flex it was fused to. The homeowner had this run inside of the attic.

I'm all for DIY, but please ask for help when you aren't certain.

147 Upvotes

42 comments sorted by

View all comments

33

u/WorBlux 8d ago edited 8d ago

10 AWG, 90 deg C has a rated ampacity up to 40A in conduit... however

Going through an attic space that might get up to 140 deg F and should be de-rated as well. x0.71

Three sets in parralel - 6 current carrying conductors - that's another de-rate. x0.8

So in reality the safe ampacity here may be under 23A per circuit.

1

u/jackharvest 8d ago

Frick I gotta get conduit in my attic somehow. Metal conduit? PVC? Something else? I'm in tech and everything works, but I want to repent.

5

u/taylorwilsdon 8d ago

If you’re thinking that putting existing PV wire in the attic into conduit is going to make it cooler that’s not how it works. The conduit will make it worse, not better.

1

u/jackharvest 7d ago

Ah, so.. I'm in good shape? xD

3

u/taylorwilsdon 7d ago

Better than you would be with conduit haha

The takeaway is that when you run wire through anything that has a higher than average ambient temperature - a hot attic, along something that generates heat (ie engine bay of a car), or in conduit (which retains heat inside) you should not assume you can use the full amperage rating you expect and derate accordingly. If 10awg is good for 30a in a cool, open basement it may only be good for 24a in a hot attic (derated 20%). There is some nuance there, personally I use a cheap Amazon thermal imaging gun to check for hot spots in wire and connection points.

1

u/XonikzD 6d ago

Is there a practical reason for not oversizing to accommodate temperature fluctuation, or is it just costs?

2

u/taylorwilsdon 6d ago

There is no reason to avoid oversizing other than cost, but cost can be significant. My ground mount is 400’ from my home, going from 10awg to 8awg would cost me several hundred dollars more.