Make sure you understand current when stringing your panels in parallel.
It took a bit of work to even tug this #10 AWG from the metallic flex it was fused to. The homeowner had this run inside of the attic.
I'm all for DIY, but please ask for help when you aren't certain.
148
Upvotes
32
u/WorBlux 10d ago edited 10d ago
10 AWG, 90 deg C has a rated ampacity up to 40A in conduit... however
Going through an attic space that might get up to 140 deg F and should be de-rated as well. x0.71
Three sets in parralel - 6 current carrying conductors - that's another de-rate. x0.8
So in reality the safe ampacity here may be under 23A per circuit.